Subscriber access issue
MAHINDBA
Posted messages
7
Status
Member
-
MAHINDBA Posted messages 7 Status Member -
MAHINDBA Posted messages 7 Status Member -
Hello everyone,
I am facing a connection problem between a laptop (Windows 7) and a Siemens S7 1214 PLC via Ethernet.
Let me explain the situation a bit more,
I need to program my PLC which is blank, and for that, I have connected my laptop directly to the PLC. Windows detects an unknown network, and I went to the Network and Sharing Center, the diagram indicates that the connection is not reaching the network.
I then performed a ping test to verify, first using auto IP and then with the fixed IP recommended by Siemens (which is 192.168.0.99). In both cases, the result is the same:
"cannot reach the destination host".
I find myself at an impasse and since this is a PLC that controls safety devices, I cannot afford to spend 2 weeks looking for the solution alone.
That's why I am reaching out to your knowledge and kindness to help me a bit
Thank you all for your attention.
I am facing a connection problem between a laptop (Windows 7) and a Siemens S7 1214 PLC via Ethernet.
Let me explain the situation a bit more,
I need to program my PLC which is blank, and for that, I have connected my laptop directly to the PLC. Windows detects an unknown network, and I went to the Network and Sharing Center, the diagram indicates that the connection is not reaching the network.
I then performed a ping test to verify, first using auto IP and then with the fixed IP recommended by Siemens (which is 192.168.0.99). In both cases, the result is the same:
"cannot reach the destination host".
I find myself at an impasse and since this is a PLC that controls safety devices, I cannot afford to spend 2 weeks looking for the solution alone.
That's why I am reaching out to your knowledge and kindness to help me a bit
Thank you all for your attention.
1 answer
-
Hi,
what fixed IP have you configured on your PC?
what is the default IP address of the PLC?
if it is DHCP by default, you also need a DHCP server on the PC in addition to the fixed IP.
--
and ... there you go!-
My fixed IP address is 192.168.0.99 with a subnet mask of 255.255.255.0 for the Realtek PCie Gbe family controller (Network cable not connected).
The IP address of the device is 192.168.0.1 with a subnet mask of 255.255.255.0.
And when I want to go online, it tells me that it is impossible to find an accessible subscriber on the selected network. -
-
now I just want to establish the connection online (virtually) without an automate or an Ethernet cable.
but when I initiate the connection, they told me it's impossible to find an accessible subscriber.
and I tested it with the CPU 315 just to try. and I take the type of the PC/PG MPI interface.
and the PC/PC PLCSIM interface
and the interface with the MPI network interface. but I got the same problem. -
-
-